I'd agree with most of what eugendakin said, with the exception of their use as control valves, if by control he means modulating flow. This is sometimes done, but it is definitely not an appropriate use of butterfly valves. The flow characteristic for a butterfly valve is such that typically the valve would need to close 50% or more before seeing any significant reduction in flow. This implies that for most modulating control situations, the valve will only be operating at 20-35% open or so. This, by the way, is also mostly true of full-port or standard-port (uncharacterized) ball valves. However, a number of the ball valve manufacturers will install inserts into their ball valves to provide characterization to their flow profiles, and that can be tuned for specific flow applications. To my knowledge, this is not possible with butterfly valves.
That's not to say that a butterfly can't be used in special control circumstances, only that you should be aware of the limitations.
If by control he means on/off actuation, this is a very common and appropriate use of either butterfly valves or uncharacterized ball valves.